RV pedistal at the house

I have a 30 amp pedestal at my home for the RW... Its been there for 20 years , and I am 100% clueless when it comes to electric..
I want to upgrade that box to 50 amp... Here is what I DO KNOW -
1- I need a 50 amp/double pole breaker
2- I need #6 wire for the run
3- I need a 50amp outlet outside on the pole..

I DONT KNOW - Are these Redwoods wired for 240 .. OR 110 ??
__________________
2020 F-350
2020 3991RD with-
17.5 Goodyear 114's , Titan Disc brakes, MorRyde 8K IS, Onan 6.5..
Ford truck guy is offline   Reply With Quote
Old 08-17-2016, 06:13 PM   #2
Senior Member
 
xtasee's Avatar
 
Join Date: Oct 2015
Posts: 500
I did it in my hangar. They are two 110V legs. Not 240
__________________
Larry, Stephanie Park City, Utah
2017 31SL King, 8K axles, Disc Brakes,17.5 Goodyear H tires,BU Camera,5.5 Onan, Heated HT pads, Two Uniguard Awnings, Slide Toppers, 2000w PSW inverter
xtasee is offline   Reply With Quote
Old 08-17-2016, 09:13 PM   #3
Senior Member
 
johnboytoo's Avatar
 
Join Date: Jul 2013
Posts: 2,055
And IF you hire an electrician, make sure he undertands it's for an RV and knows what he is doing or else your rv won't like it at all !
__________________
Ours: '11 Monaco Diplomat 43DFT followed closely by '14 Jeep 4 dr Wrangler.
Hers: '13 Explorer Sport - AWD 365hp twin turbo scooter!
Previous: '13 Ford F350 CC Platinum and '13 38GK
johnboytoo is offline   Reply With Quote
Old 08-17-2016, 09:18 PM   #4
Senior Member
 
Ford truck guy's Avatar
 
Join Date: Jul 2015
Posts: 2,285
Quote:
Originally Posted by johnboytoo View Post
And IF you hire an electrician, make sure he undertands it's for an RV and knows what he is doing or else your rv won't like it at all !
yea , about that....

My best friend owns an electrical company... He does residential and commercial... He looked at it , and has never wired an RV before... While I DO TRUST him . . . I have hesitations of allowing him to do it.. Let's just say he was not convincing . . . and he has never stepped foot in an RV before...
__________________
2020 F-350
2020 3991RD with-
17.5 Goodyear 114's , Titan Disc brakes, MorRyde 8K IS, Onan 6.5..
Ford truck guy is offline   Reply With Quote
Old 08-17-2016, 09:20 PM   #5
Senior Member
 
5th_Time's Avatar
 
Join Date: Mar 2012
Posts: 1,136
If you have the Onan, run a second leg back to the service, install a transfer switch, and use your generator to power the house.
__________________
Mike & Pam '12 36RL, Kodiak Discs, 17.5" G114s H-Rated, SRE4000 w/HD Shackles, Joy Rider Shocks, Flex Air, 5.5 Onan, W&D, DW, 4 Scare Lights, (2) 6V Trojan T-145s; Progressive EMS-HW50C, Winegard DTV Sat, Sony/Denon 4K Home Theater, WiFiRanger EliteAC Pack, weBoost 4G-X Cell Booster.

2022 RAM 3500 Limited CC, LB, 4x4, DRW, Max Tow, Cummins HO, AISIN, 4.10, Mopar 30K w/OEM Prep, Transfer Flow 70gal Aux Tank/Toolbox.
5th_Time is offline   Reply With Quote
Old 08-17-2016, 10:58 PM   #6
Site Team
 
piper guy's Avatar
 
Join Date: Dec 2012
Posts: 1,986
Joe ~ I just had a 50a plug added to the house. The electrician that did it, looked at the plug for the coach and said "same box and wiring as a 240 volt dryer outlet" I'm guessing he was correct as my Progressive protector fired up and was happy with the install. Rig is sitting here as I write this with both AC on as I'm getting ready to do some more stuff .........
__________________
Vaughan & Tracy 2013 RW 36RL, 2013 F350 DRW CC, 2016 Focus. MorRyde IS, MorRyde pinbox, disc brakes, Comfort Ride Hitch. "Life is to be embraced, Grab it with both arms ! "
piper guy is offline   Reply With Quote
Old 08-18-2016, 12:30 AM   #7
Senior Member
 
Jim & Mary's Avatar
 
Join Date: Jul 2013
Posts: 721
Well, it can't be a "dryer outlet", as a dryer is only a 30A circuit. He should have said a range receptacle, which is a 50A circuit. Some early range receptacles were only a 3 wire type, but most modern ranges utilize a 4 wire configuration.
__________________


Jim & Mary 2013 36 RL with Titan Disc Brakes Residential Fridge Goodyear 17.5 H rated tires MORryde IS, MORryde pin box 2015 Ford F350 King Ranch DRW
Jim & Mary is offline   Reply With Quote
Old 08-18-2016, 12:31 AM   #8
Senior Member
 
Join Date: Jul 2015
Posts: 377
Just remember that the trailer is like a big toaster, all wires return to the main box. That means that the ground wire even returns to the main electrical box. You wouldn't plug in a toaster then take the ground an the neutral wire and connect it into the sink .
__________________
2013 Redwood 36RL. 2005 Dodge 3500 DRW 4X4. 6 speed manual transmission. South Bend dual disc clutch.
Tomkidder is offline   Reply With Quote
Old 08-18-2016, 12:33 AM   #9
Senior Member
 
Shane Wood's Avatar
 
Join Date: Nov 2014
Posts: 2,032
Send a message via AIM to Shane Wood Send a message via MSN to Shane Wood Send a message via Yahoo to Shane Wood
Our Redwood 50 Amp plug is 120/240 Volt
__________________
2015 36RL pushing a 2015 Denali
Shane Wood is offline   Reply With Quote
Old 08-18-2016, 12:37 AM   #10
Senior Member
 
Join Date: Jul 2015
Posts: 377
Your house should be wired 220. I believe 240 is industrial and normally comes 3 phase as they split the 440. I am not an electrician that's for sure but I wired my own pedestal at my home
__________________
2013 Redwood 36RL. 2005 Dodge 3500 DRW 4X4. 6 speed manual transmission. South Bend dual disc clutch.
Tomkidder is offline   Reply With Quote
Old 08-18-2016, 12:38 AM   #11
Senior Member
 
mhs4771's Avatar
 
Join Date: Jan 2012
Posts: 2,807
If you're running some distance, you can run just 3 wires to your post, then add a ground rod for you fourth connection. Just recently finished mine, complete with sewer and water. Ran the two hots and neutral from the main panel and added an 8' ground rod and cable at the post.
__________________
Michelle & Ann
2018 Chevy 3500HD Crew Cab High Country DRW, D/A, 2016 RW39MB, Dual ACs, Auto Level, Auto Sat Dish, Stack W/D, King Sleep #, 17.5" Sailuns w/Disc, MORryde IS & Pin, Comfort Ride Hitch, 5.5 Onan, Res Fridge & Induction Cook Top
mhs4771 is online now   Reply With Quote
Old 08-18-2016, 12:54 AM   #12
Senior Member
 
Shane Wood's Avatar
 
Join Date: Nov 2014
Posts: 2,032
Send a message via AIM to Shane Wood Send a message via MSN to Shane Wood Send a message via Yahoo to Shane Wood
Tom
I have been supplying electrical service to everything working as a Lineman in the electrical utility industry. Every house today is fed 120/240 volts from the transformer. Commercial load which uses 3 phase to run motors has 3 hot phases that measure 240 volts across any of the 3 and 2 of them me sure 120 volts to neutral or ground and the third measures 208 volts to ground. Totally different service.
Xtasee
If you take a voltmeter and measure the voltage across the 2 hot legs you will get 240 volts. If you measure from ground to either one you will get 120 volts. Everything in the trailer is 110 volt. With a 50 amp service you have 100 available amps 50 amps on each 120v wire
__________________
2015 36RL pushing a 2015 Denali
Shane Wood is offline   Reply With Quote
Old 08-18-2016, 03:57 AM   #13
Senior Member
 
Join Date: Jan 2016
Posts: 325
All houses have 120 / 240 volt. You get the 240 volt by having 2 phases. A and B phase. In you home items as your stove - dryer electric - heating run on 240 volt. By using both A & B to run these items that is why you have 2 pole breakers in your house and not in the RV except for the entrance breaker. Actually all RVs you are only using 120v. You need 2 black from A & B plus a white and a green ground. This should not confuse an electrician. The configuration of the plug is the type it is due to the industry choosing that "nema" type plug. Make sure the box outside you use is waterproof and if it is a long run have the voltage drop calculated as you may only be delivering 100 volts at the plug and need an even larger wire size. As long as you wire your pedistal properly your RV will be ok. Also don't start trying to figure 3 phase as you should only have that at work not at a residence. As for the ground rod approach. I would not suggest it with all the electronics we use in these units today. You want a clean connection. Also one reason if should the grid should drop a phase the neutral can become live and not having a true ground you do not have full protection from that happening. Then you fry things.
__________________
Meet Teddy Bear
Make Every Day Count
2016 Denali 3500 Diesel SRW
2015 38 GK
Cheryl & Wayne
ted 95 is offline   Reply With Quote
Old 08-18-2016, 12:36 PM   #14
Senior Member
 
Join Date: Jul 2015
Posts: 377
I have learned a bit more about household electricity Thanks. I find it very interesting how all in one place we have a small army of people from every occupation imaginable, freely enlisted and linked together, offering....... Some of the best advice. As I read through the pages of this forum (and have read thousands) I learn all kinds of things from a different prospective. All of this is what makes this forum so great. I have subscribed to many other forums and found mountains of information on various topics. This forum by far is my favorite. The information that is given, and debated here is done so in such a manor that is more teaching than finger pointing at some one with way less knowable experience. For all of this I would really like to thank you all for your contributions. (If people only knew what we have here and how it is managed every RVer would want to be on this forum).
__________________
2013 Redwood 36RL. 2005 Dodge 3500 DRW 4X4. 6 speed manual transmission. South Bend dual disc clutch.
Tomkidder is offline   Reply With Quote
Old 08-18-2016, 01:16 PM   #15
Senior Member
 
Ford truck guy's Avatar
 
Join Date: Jul 2015
Posts: 2,285
Thanks to All who helped , and answered.. I passed on the info to my friend , and he fully understands how it needs to be run...

I too think this forum is great ! ! between learning things , and meeting great folks , its a win-win.!
__________________
2020 F-350
2020 3991RD with-
17.5 Goodyear 114's , Titan Disc brakes, MorRyde 8K IS, Onan 6.5..
Ford truck guy is offline   Reply With Quote
Old 08-18-2016, 01:46 PM   #16
Senior Member
 
mhs4771's Avatar
 
Join Date: Jan 2012
Posts: 2,807
Back to the Ground Rod issue. If you look at the wiring coming into you home you will find only three wires, L1, L2, and Neutral. Somewhere just outside you home where the Power Meter is there will be 2 grounds rods connected via cable which goes into the meter to provide the Earth Ground.
__________________
Michelle & Ann
2018 Chevy 3500HD Crew Cab High Country DRW, D/A, 2016 RW39MB, Dual ACs, Auto Level, Auto Sat Dish, Stack W/D, King Sleep #, 17.5" Sailuns w/Disc, MORryde IS & Pin, Comfort Ride Hitch, 5.5 Onan, Res Fridge & Induction Cook Top
mhs4771 is online now   Reply With Quote
Old 08-18-2016, 03:57 PM   #17
Senior Member
 
johnboytoo's Avatar
 
Join Date: Jul 2013
Posts: 2,055
Yep - had stubbed my toe on that one at the old house more than once when cutting grass


And why I'm just trying to help with my earlier warning of 'it's different' and be careful who does it - there have been reports on other sites of 'regular' electricians frying rv electronics...

and the different opinions on this thread is an example of the differences
__________________
Ours: '11 Monaco Diplomat 43DFT followed closely by '14 Jeep 4 dr Wrangler.
Hers: '13 Explorer Sport - AWD 365hp twin turbo scooter!
Previous: '13 Ford F350 CC Platinum and '13 38GK
johnboytoo is offline   Reply With Quote
Old 08-18-2016, 04:01 PM   #18
Senior Member
 
Ford truck guy's Avatar
 
Join Date: Jul 2015
Posts: 2,285
also know those very well... When we upgraded to our underground/200amp service my friend that is a lineman just drove his bucket truck over with trencher , and all the supplies...

MY main job was to pound those rods 8' under! did 2 at the house , 3 at the pool ,and 1 at the pool outlet pole...
__________________
2020 F-350
2020 3991RD with-
17.5 Goodyear 114's , Titan Disc brakes, MorRyde 8K IS, Onan 6.5..
Ford truck guy is offline   Reply With Quote
Old 08-18-2016, 05:55 PM   #19
Senior Member
 
atom ant's Avatar
 
Join Date: Feb 2013
Posts: 7,101
The 50A 240/V at your range is no different than your campground pedestal, your range is just configured to use 240V, and your Redwood is not.

30A is a different animal, the 30A RV outlets were unique to RVs and only have one 110V leg.

With that, you can modify your Redwood to accept a 240V dryer, or even a range. The downside is you would lose those appliances at a 20A or 30A site.

I hear rumor some new high end RVs are starting to utilize 240V, and I even heard some are so large and consuming they have went to 100A/240V service, but I haven't seen one yet. I think the idea is they can plug into any 50A service and get their 240V, but when 100A happens to be available in the future they can run full capacity.
__________________
Brad & Dory - Lone Tree, CO
CURRENT - 2013 Itasca Meridian 42E/2013 Wrangler 4dr Sahara
SOLD - 2014 Redwood 36RL/2014 F350 DRW
atom ant is offline   Reply With Quote
Old 08-21-2016, 02:46 AM   #20
Senior Member
 
Join Date: Aug 2014
Posts: 191
240v

The post should be wired as a 240V outlet, but your RW will only use 2 120 v legs. Inside the connector the voltage between the black and red wires is 240 v. From red to white (neutral) is 120 V and from black to white is also 120 v. the 110 v (or 115 v) commonly referred to is usually measured a little higher and is now generally called 120 v. Make sure the electrician wires the green wire (or bare copper) which is ground. Your coach has a chassis ground and relies on the post's power ground to provide a safely ground.

I wish I could have power to my 38RL, but my HOA won't allow me to have it at my house.
__________________
2015 38RL with MORryde IS, residential fridge, DW, washer and dryer, generator, and slide in slide. 2 A/C, 1 HP and a fireplace. Added 17.5 inch wheels. Follows a 2013 Ram dually diesel with 8' bed and Reese 20K.
RW Cal is offline   Reply With Quote
Reply


Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by Redwood RV or any of its affiliates. This is an independent, unofficial site.


All times are GMT +1. The time now is 02:43 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
×