Old 11-28-2015, 05:29 PM   #1
Senior Member
 
Jim & Mary's Avatar
 
Join Date: Jul 2013
Posts: 721
Heat pump cb tripped

Our heat pump 20A breaker tripped this morning. Waited a bit to cool down. It is currently drawing 17.5 A and slowly rising. The breaker is physically warm to the touch after tripping. Data sheet shows 15.4 A running current. Any thoughts anybody?
__________________


Jim & Mary 2013 36 RL with Titan Disc Brakes Residential Fridge Goodyear 17.5 H rated tires MORryde IS, MORryde pin box 2015 Ford F350 King Ranch DRW
Jim & Mary is offline   Reply With Quote
Old 11-28-2015, 05:38 PM   #2
Senior Member
 
Join Date: Jul 2015
Posts: 377
Is the wire tight in the CB. Other things to look for are weak start/run capacitors in the unit also the blower fan may have a bearing starting to go bad and the unit has to draw mor power.
Tomkidder is offline   Reply With Quote
Old 11-28-2015, 09:55 PM   #3
Senior Member
 
Jim & Mary's Avatar
 
Join Date: Jul 2013
Posts: 721
Found the exact 15/20 A breaker (Siemens) at home depot for less than $12. Replaced, so we'll see if that does the trick. Don't want to think about the next step if it doesn't.
__________________


Jim & Mary 2013 36 RL with Titan Disc Brakes Residential Fridge Goodyear 17.5 H rated tires MORryde IS, MORryde pin box 2015 Ford F350 King Ranch DRW
Jim & Mary is offline   Reply With Quote
Old 11-29-2015, 04:15 AM   #4
Member
 
scott&phyllis's Avatar
 
Join Date: Jul 2014
Posts: 41
Did you check the voltage coming into the RW? If you have low voltage coming in, the amps will be higher than should be.
scott&phyllis is offline   Reply With Quote
Old 11-29-2015, 03:06 PM   #5
Senior Member
 
Jim & Mary's Avatar
 
Join Date: Jul 2013
Posts: 721
Pretty sure voltage is ok, as we have the progressive industries hard wired surge protector. It would have shut down on low or high voltage.
__________________


Jim & Mary 2013 36 RL with Titan Disc Brakes Residential Fridge Goodyear 17.5 H rated tires MORryde IS, MORryde pin box 2015 Ford F350 King Ranch DRW
Jim & Mary is offline   Reply With Quote
Old 11-29-2015, 05:29 PM   #6
Senior Member
 
Jim & Mary's Avatar
 
Join Date: Jul 2013
Posts: 721
Well, I find I must now eat my words. We were enjoying coffee this morning and the surge suppressor (Progressive Industries EMS-HW50C) shut the Redwood down and the code was PE6, low voltage on Line 2. Pedestal power was still only about 109 volts after restored power, so guess we'll go try and plead with the park to fix. Line 1 voltage is 122. So the original trip must have been because of low voltage. The heat pump was drawing 17.6 yesterday, but today is at 14.4 so perhaps the suppressor saved the day.
__________________


Jim & Mary 2013 36 RL with Titan Disc Brakes Residential Fridge Goodyear 17.5 H rated tires MORryde IS, MORryde pin box 2015 Ford F350 King Ranch DRW
Jim & Mary is offline   Reply With Quote
Old 11-29-2015, 05:58 PM   #7
Site Team
 
hoosierguy's Avatar
 
Join Date: Nov 2011
Posts: 1,340
Quote:
Originally Posted by Jim & Mary View Post
Well, I find I must now eat my words. We were enjoying coffee this morning and the surge suppressor (Progressive Industries EMS-HW50C) shut the Redwood down and the code was PE6, low voltage on Line 2. Pedestal power was still only about 109 volts after restored power, so guess we'll go try and plead with the park to fix. Line 1 voltage is 122. So the original trip must have been because of low voltage. The heat pump was drawing 17.6 yesterday, but today is at 14.4 so perhaps the suppressor saved the day.

I am curious............what is the ampere rating of the circuit breaker for that heat pump?
__________________
Guy & Phyllis
2012 RW36RL,DualA/C,KodiakDiskBrakes,TrailAir Tri-Glide,GY_G614's,Roadmaster Comfort Ride Slipper Spring Suspension
2011Dodge3500Laramie,CrewCab,4x4,SRW,Michelins, LongBed,6.7LCTD,3.73,PullRiteSuper5th20.5KHitch, BlueOxBedsaver

hoosierguy is offline   Reply With Quote
Old 11-29-2015, 06:06 PM   #8
Senior Member
 
atom ant's Avatar
 
Join Date: Feb 2013
Posts: 7,101
Quote:
Originally Posted by Jim & Mary View Post
Well, I find I must now eat my words. We were enjoying coffee this morning and the surge suppressor (Progressive Industries EMS-HW50C) shut the Redwood down and the code was PE6, low voltage on Line 2. Pedestal power was still only about 109 volts after restored power, so guess we'll go try and plead with the park to fix. Line 1 voltage is 122. So the original trip must have been because of low voltage. The heat pump was drawing 17.6 yesterday, but today is at 14.4 so perhaps the suppressor saved the day.
There you go! Don't you love those things? I wish I would have installed the display.
__________________
Brad & Dory - Lone Tree, CO
CURRENT - 2013 Itasca Meridian 42E/2013 Wrangler 4dr Sahara
SOLD - 2014 Redwood 36RL/2014 F350 DRW
atom ant is offline   Reply With Quote
Old 11-29-2015, 06:19 PM   #9
Senior Member
 
Jim & Mary's Avatar
 
Join Date: Jul 2013
Posts: 721
Guy

That is a 20 A rating for the heat pump/ AC. Both rooftop units are 20 circuits. They put that breaker with a 15 A breaker in the same package.
__________________


Jim & Mary 2013 36 RL with Titan Disc Brakes Residential Fridge Goodyear 17.5 H rated tires MORryde IS, MORryde pin box 2015 Ford F350 King Ranch DRW
Jim & Mary is offline   Reply With Quote
Old 11-29-2015, 11:47 PM   #10
Senior Member
 
Join Date: Jul 2015
Posts: 377
Mine just popped the breaker today also. I checked the voltage and all is well. I have the unit plunged into my house. I am going to be watching this a little more careful. If I have a continued problem it will be trouble shooting time. It is raining today so I thought I would sit in the house and think about it. There is just something about electricity and water that makes me a little more nervous than normal.
Tomkidder is offline   Reply With Quote
Old 11-30-2015, 04:01 AM   #11
Member
 
scott&phyllis's Avatar
 
Join Date: Jul 2014
Posts: 41
Quote:
Originally Posted by Jim & Mary View Post
Well, I find I must now eat my words. We were enjoying coffee this morning and the surge suppressor (Progressive Industries EMS-HW50C) shut the Redwood down and the code was PE6, low voltage on Line 2. Pedestal power was still only about 109 volts after restored power, so guess we'll go try and plead with the park to fix. Line 1 voltage is 122. So the original trip must have been because of low voltage. The heat pump was drawing 17.6 yesterday, but today is at 14.4 so perhaps the suppressor saved the day.
Glad no damage to your rig. The Progressive did its job. I would not be without my Progressive either. Always use it, even when plugged in at home.
scott&phyllis is offline   Reply With Quote
Reply


Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by Redwood RV or any of its affiliates. This is an independent, unofficial site.


All times are GMT +1. The time now is 03:11 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
×